otis 211 DCP error

34 Posts
1 Users
0 Reactions
80.7 K Views
(@sbrmilitia)
Joined: 1 second ago
Posts: 0
 
Otis is green.......hope I don't get banned



   
ReplyQuote
(@kiwinightstalker)
Joined: 1 second ago
Posts: 0
 
Originally Posted By: ThyssenKrapp
Ha it was just the easiest name to parody! i assumed that "swindler" was already taken

And yes i have worked for them in the past as i have for 3 out of the 4 majors

TK were not that bad to work for probably the "best of a bad bunch"

Anyway what was the cause of the DCP error??

Yuuuup worked for Thyssen also ....wish I still was!!!!! but for circumstances beyond of MY control sadly no longer do!!!

Last edited by kiwinightstalker; 07/10/13 12:00 PM.


   
ReplyQuote
(@mike_zll)
Joined: 1 second ago
Posts: 0
 
hello

Check the light curtain and door systems。
modify DCP parameters to 255。



   
ReplyQuote
 Len
(@Len)
Joined: 1 second ago
Posts: 0
 
check your parameters..always good to set Dcp to a higher value than Dtc is set...enable the tone for the door detector this will tell you if there is a problem with the detector false firing..last but not least check and make sure your door operator is seeing the DOL input..depending on what operator you have you could have a bad sensor...or need to learn run..if the counts have changed...



   
ReplyQuote