The elevator intermittently gets a temp fault and returns to the lowest landing. There are no temp switches connected to the controller. What else other than a temp sensor would cause a temp failure? The book doesn't really offer any info. Thanks for the help!!!
15/05/2012 4:43 am
Dont know much about the MPH2....if it has a thermal overload on P1 to P2 on the pump motor could this be opening up? That is if it is a self reseting thermal or maybe a loose wire on the thermal on the motor maybe?
15/05/2012 7:35 am
There's a thermal and/or bi metallic contact in the 5 & 11A circuit, are they jumped?
Topic starter
15/05/2012 8:16 am
I think I have it figured out. I referred back to a post that Dan Zeitz wrote about an MPHI that had a similar issue. If the computer doesn't see the K55 input then the elevator will fault out with a Temp Failure after a period of time. In his case it was 13 seconds. I wasn't really paying attention to the run time when I was on the job but I did notice it would fail more often on longer runs than short runs. A while ago, another company installed a solid-state starter and I think they may have mis-wired this circuit when they removed the wye-delta configuration. I'll be back to the job tomorrow to check it out. Wish me Luck!!!
15/05/2012 9:46 pm
Low oil/AST has the same outcome.
16/05/2012 2:35 am
Sounds like your on it!
Topic starter
16/05/2012 10:40 am
Ok, went back to the job. Just as suspected, the signal wires for the K55 input were taped up in the bottom of the controller under the solid-state starter. I'm glad Danzeitz posted that proplem, this one could have had me going for a while. Thanks for the help!!!!!