I understand that this is a MSU "BCI" (Balance Complete Input) that originates from the drive "Motion adapter" board
with the ribbon cables it's difficult to meter this signal
I have re seated ribbon cables, boards, changed both "BCX" and "BC" relays with no luck
I'm leaning towards faulty "Motion Adapter" board in drive
Is there something else I should be looking at that this "BCI" input monitors that I can check?
Thanks for any suggestions
NC aux M contacts meter good but the M contact never pulls in to check NO aux contacts.
I was under the impression that because I have a DDC and not a anolog drive( uses aux M contacts) that my BC signal is originated from drive then routed back to MSU board through BCX and the MC contacts
I'm looking at some prints now...looks like I may have overlooked a BJ1 pilot relay that is right before BCX....and if I recall correctly I believe the job specific prints(500 FPM) at building shows my ETS circuits running through M aux contacts(which may explain why none of the ice cube relays are lit up but my high and lo voltages are good to board)
Thank you Sir
I don’t know what all is envolved with the drive picking K3 though, maybe someone else knows more about it.
Miprom21...out of those3, P2 is the only one that does pull in, I haven't bothered metering the NO NC contacts on it as I've been focused on the "No BC Feed Back" fault and the related circuit....now you have me thinking it's one of the NO or NC P2 circuits, I will find out tomorrow and follow up
Good luck
With elev on 2nd landing I had a mis match with Red led NTSI input off and Green ETS output on...it was difficult to troubleshoot the ETS boards in bottom of controller with original ice cube relays, hard to tell if they were picked or not so I replaced them all along with the ETS and NTS ones on upper swing panel board with the user friendly IDEC ones with LED and the elevator took right off, observed operation for an hour with no issues.
Wish I could report what the smoking gun was and issue may vary well come back.
Someone did mount a ice cube relay that when pushed it pulled in M contactor(nice way to verify good coil)....didn't trace wires out so not sure what the purpose was
Hats off to the Gents with all the Miprom knowledge....those can be a real Bear!