mce-imc. PR error (binary floor code )

7 Posts
3 Users
0 Reactions
9,857 Views
(@jimbonj)
Estimable Member
Joined: 17 years ago
Posts: 67
Topic starter   [#22800]
Hi guys. We get this error about every 48hrs on the 8th floor where it homes -15 stop car - changed tape guides and Pr sensor in LS-quad unit. - on 8th floor we have all 3 led's lit (rd-pr-r3) on controller ) even swapped triacs on leveling box (pr with the rd triac) and still no luck



   
Quote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
I’d probably replace the R3 sensor and triac too. I think if it went low it would throw that error since there would be an odd parity, same for another sensor failing closed. I’m sure you’ve checked the magnets at that floor, also check traveler and ribbon cables taking the signals from SCR-RI to DIO and DDP boards. Maybe wiggle connections while watching the inputs.



   
ReplyQuote
(@jimbonj)
Estimable Member
Joined: 17 years ago
Posts: 67

   
ReplyQuote
(@jimbonj)
Estimable Member
Joined: 17 years ago
Posts: 67

   
ReplyQuote
(@upanddown2321)
Trusted Member
Joined: 17 years ago
Posts: 96
 
It shouldnt be correct because of parity, but if it says 12 its possible R2 is an issue. As R3 and R2 would code floor 12 instead of 8



   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759

   
ReplyQuote
(@jimbonj)
Estimable Member
Joined: 17 years ago
Posts: 67

   
ReplyQuote