LRV 5L

7 Posts
1 Users
0 Reactions
6,677 Views
(@Jluff)
Joined: 1 second ago
Posts: 0
Topic starter   [#20753]
LRV 5L

Had power problems in building
Doors r dead
No power to HES coils
No power to 20CI 1 thru 6
All Saftey circuits good
All fuses n power r good.
110v to 11CI 10 but don't power to 20CI 6
Think board is bad.
F2 fuse did not blow which is weird to me
What do u guys think ?



   
Quote
(@JHessorz)
Joined: 1 second ago
Posts: 0
 
Looks like door power comes right off taps of the transformer (PSD1-PSD2) and gets fused and rectified and sent straight to the operator. Did you diode check the rectifier and confirm your voltage to it?



   
ReplyQuote
(@Jluff)
Joined: 1 second ago
Posts: 0
Topic starter  
No. But I will. I think I ruled out the rectifier but don't remember why.
Txs JH



   
ReplyQuote
(@Indirtwetrust)
Joined: 1 second ago
Posts: 0
 
When you say doors are dead, do DO and DC pick but doors don't move? You are only going to read voltage on 20CI-6 if DO and AUD are both picked. And are you saying NDG is picked but you have no voltage to HES? Does the car run on inspection?



   
ReplyQuote
(@Indirtwetrust)
Joined: 1 second ago
Posts: 0
 
If none of the ice cube relays are picking, make sure you have 24vdc at DC6 through the F6 fuse. That 24v regulator on the board is a weak point. If it fails it can just be removed.



   
ReplyQuote
(@chicago)
Joined: 1 second ago
Posts: 0
 
Car station capacitor needs to be discharged, it locks elevator up.



   
ReplyQuote
(@Jluff)
Joined: 1 second ago
Posts: 0
Topic starter  
Txs Chicago. That was it.



   
ReplyQuote