Kone KCM 831

2 Posts
2 Users
0 Reactions
2,017 Views
(@danzeitz)
Prominent Member
Joined: 17 years ago
Posts: 672
Topic starter   [#18331]
We ave a triplex group that would intermittently put any given car on earth quake operation. After going thru everything to do with earthquake we disconnected the 3 wire feed to a remote panel as a process of elimination and the problem went away. This remote station is a 300ft run from the hoist-way in a parking garage. There is a line repeater located In The Controller???? Is this right??? or should the repeater be further down the line????? Thanks Dan



   
Quote
(@lowoil)
Reputable Member
Joined: 17 years ago
Posts: 270
 
Yup,when I did a 19 stop with 31 floors we put in I think 3 repeater boards through out the hoistway,I'd have to look in a install manual.



   
ReplyQuote