These elevators are fairly new, about 6 or 7 years old. We've had them on service about two years, I think.
My associate thinks the oil is too cold. Because after running it for several runs, it then started stopping correctly. It has an oil cooler, and so he changed the thermostat setting today.
We had this problem a year ago, and when I reccomended a tank heater to the customer, he remarked that the two adjacent units had no problems, so why would this unit need one?
Interesting to note, that on the thrid unit in the same machine room, the OEM removed their own Hydro-Morris valve, and replaced it with a Maxton. That's very telling, when they change out their own installed brand of valve, for a Maxton.
Anyway, and ideas are sincerely appreciated!
Ok, except this looks like a cold oil problem. We'll try for the Maxton fix, sounds best.
yeah vic i/we always try to look like we arent trying to rip customers off and by saying we will cover the cost if it doesnt work it shows this. i must admit ive never worked on a modern hydro without these block or oil heaters and this cold oil can also cause a relevel fault when the lift drops below level. very common fault that heater(and floor level tuning) can rectify.