Might need some help on this one.

Newer Kone ecospace with adon 2 board...
Call comes in every other week or so. Stuck at the bottom floor with the following faults.
74
170
108
44

So far we have swapped LD sensor with LU. Done shaft learn and adon learn. Problem still persists.

Any input guys?



   
Quote
(@steveo)
Eminent Member
Joined: 17 years ago
Posts: 34
 
74-61N is stuck
170-AC voltage failure....seen when disconnect is cycled.
108- speed difference, sub code would really be helpful.
44-doors tried to close too many times

What drive is it?



   
ReplyQuote
(@scott-davidson)
Honorable Member
Joined: 17 years ago
Posts: 402
 
i have only worked on a few of the kone geared cars, one thing that i found interesting is that if you look at the LCE computer when you are scrolling thru the faults and sub codes, keep an eye on the led"s of the input and outputs of the LCE unit, they will show you the status of the led at the time of the fault, at least this is what i think i saw. maybe you can see 61:n signal still on, just a little input, i have had that fault before, and we swapped lu an ld sensors, and the problem just disappeared . damn elevators anyway



   
ReplyQuote
(@scott-davidson)
Honorable Member
Joined: 17 years ago
Posts: 402
 
i have only worked on a few of the kone geared cars, one thing that i found interesting is that if you look at the LCE computer when you are scrolling thru the faults and sub codes, keep an eye on the led"s of the input and outputs of the LCE unit, they will show you the status of the led at the time of the fault, at least this is what i think i saw. maybe you can see 61:n signal still on, just a little input, i have had that fault before, and we swapped lu an ld sensors, and the problem just disappeared . damn elevators anyway also, if you log onto the unit with a laptop, you can get some extra info also, in the fault log, it is probably the same as the extra info you get in the sub codes, but it couldnt hurt to take a look at the log.



   
ReplyQuote
(@aquadag)
Estimable Member
Joined: 17 years ago
Posts: 173

   
ReplyQuote
(@elevator-steve)
Eminent Member
Joined: 17 years ago
Posts: 36
 
It's possible the issue starts with the 170 power loss fault. Check connections in controller (transformer, power supply, etc.). It could be losing a leg of the 3 phase somewhere.



   
ReplyQuote
(@aquadag)
Estimable Member
Joined: 17 years ago
Posts: 173

   
ReplyQuote
(@classic-chevy)
Trusted Member
Joined: 17 years ago
Posts: 37
Topic starter  
The problem is the 108 fault. Car runs all day long without any weight in the car. Put 50% of the load and the car gets a 108 fault coming into the bottom floor. Load weighing is adjusted properly. If I tune the load weighing down to read less than 50% (43% to be exact). The car will make the bottom floor no problem. But then it gets a 108 fault trying to leave the floor. The other faults listed were symptomatic of the 108 fault. 108 is a motor tachometer fault but car runs flawlessly empty car top to bottom and anywhere in between. Also, I have never seen channel faults on the ADON board so the tach has been ruled out. Load weighing board and drive swapped with no change. Seems like the pattern is hitting a torque or current limit coming into the floor. But why only at the bottom floor with a balanced car? Doesn't make a lot of sense. Aqua dog. Any ideas?



   
ReplyQuote
(@elevator-steve)
Eminent Member
Joined: 17 years ago
Posts: 36
 
If the fault starts with a 74 then power cycled which gives you the170 fault. The 108 and 44 are a result of the power cycle.
For a fault 74...order a XB46 resistor plug from KONE spares and plug it into yours CCBN.
However if the 108 is first then we need sub fault code to help you. If it is only happening with load at a certain landing...check your rails at that landing.
Also check for a flat spot on your tach wheel.



   
ReplyQuote
(@elevator-steve)
Eminent Member
Joined: 17 years ago
Posts: 36

   
ReplyQuote
(@classic-chevy)
Trusted Member
Joined: 17 years ago
Posts: 37
Topic starter  
Drive parameters have been verified and car is balanced at 50%. The 74 fault is a result of the 108 fault. Car gets 3 consecutive 108 faults trying to level down into the bottom floor while on 30 and 61N and then throws a 74 fault and shuts down. Tach looks good. Resistor plug is in place at XB46. Already went down that road and definitely not a level sensor problem.



   
ReplyQuote
(@aquadag)
Estimable Member
Joined: 17 years ago
Posts: 173

   
ReplyQuote
(@classic-chevy)
Trusted Member
Joined: 17 years ago
Posts: 37

   
ReplyQuote
(@elevator-steve)
Eminent Member
Joined: 17 years ago
Posts: 36
 
What are the sub faults of the 108? While viewing the 108 press accept and it will scroll a 4 digit sub fault code...



   
ReplyQuote
(@classic-chevy)
Trusted Member
Joined: 17 years ago
Posts: 37

   
ReplyQuote