Intermittent 211 Fault

12 Posts
1 Users
0 Reactions
16.9 K Views
(@Administrator)
Joined: 1 second ago
Posts: 0
Topic starter   [#7501]
We have a newer 211 2 Stop that's been getting a (2711) "Stall Down" fault every couple of days at the 2nd Floor. Verified that the rupture valve is not setting. Valve seems to be good, never any heat issues. Once reset the car runs fine again for a couple of days. Other associated faults are: 2005, 2102, 2644. Anyone have any ideas as what could be causing this shut down.

Thanks



   
Quote
(@Scott Davidson)
Joined: 1 second ago
Posts: 0
 
i saw this a couple months ago. i gave the car a 2nd floor call, the car travels down from the 5th floor, but it seemed to slow down for the 2nd floor way to early. then it just slowly leveled into the 2nd floor took a while, car logged stld fault and shut down. replaced the tape guides, and reglued a couple magnets that had come loose. problem solved. if you have to redo magnets use the template



   
ReplyQuote
(@elmcannic)
Joined: 1 second ago
Posts: 0
 
STLD at the top floor and it's a 2 stop. Is the unit below or at floor level...can you tell?
Scott's reference to magnet position is a good one. Possibly a weak DZ magnet? A down stop limit blipping open from the previous up run? Maybe check the selector wiring in the COP. Hmmm.



   
ReplyQuote
(@Administrator)
Joined: 1 second ago
Posts: 0
Topic starter  
The mechanic on the job said the tape guides were good and lined up the magnets with the guide. Also, he said the magnets lined up to their original marks with the guide. I have had some issues with 211 selector boards on other jobs in the past. I was thinking maybe just replace the board and wait and see what happens. I'll have him check the wiring in the COP. Thanks for the suggestions!!!



   
ReplyQuote
(@sccjr)
Joined: 1 second ago
Posts: 0
 
A few ideas. I had a rupture valve iterm give me issuses until one day it failed for good w/ an entrapee, that was a fun one, but I finally found the problem after numerous calls w/ a stld fault. Also you could have a low pressure sw acting up or a sticky packing, check your down leveling speed, those otis packings are known to be a bit troublesome. The down direction limit sw's also could be a possibility.



   
ReplyQuote
(@Take the stairs)
Joined: 1 second ago
Posts: 0
 
I agree with Scott, had that problem with a 4 stop udjusted magnets at all floors , and replaced tape guides. Car hasn't had any problems since.



   
ReplyQuote
(@Derick)
Joined: 1 second ago
Posts: 0
 
make sure DA is set correctly if not it will never leave the floor in the down when the oil is cold



   
ReplyQuote
 Len
(@Len)
Joined: 1 second ago
Posts: 0
 
..Derick is right..many STLD,s are corrected by taking out on DA at least 1/2 turn...also optos on the Reader boards have shown to have problems.,and are too weak to pick-up the magnets..also a bounce in the doorlock or gate swith..while car is initiated a down input..have had this one drove me crazy...

Last edited by Len; 06/28/13 05:26 AM.


   
ReplyQuote
(@elevatedone)
Joined: 1 second ago
Posts: 0
 
Set parking for the first floor after one minute.
It relevels at the 2nd floor,overshoots then hits the limit.
I did this to all my units,when I had units.



   
ReplyQuote
(@Administrator)
Joined: 1 second ago
Posts: 0
Topic starter  
Thanks for all the tips! We've done a lot of these things. We'll have to wait to see what happens.



   
ReplyQuote
 Len
(@Len)
Joined: 1 second ago
Posts: 0
 
211's should not overshoot..limits are adjusted for 1.5"Above top landing..holeless will seep down a little bit as oil cools down...software is implemented to allow car to relevel after it is parked for a period of time..upon activation of hall call

to



   
ReplyQuote
(@Administrator)
Joined: 1 second ago
Posts: 0
Topic starter  
Good Job Derick! It was the DA adjustment that was causing the issue. I guess the oil would cool just enough during the slow time to restrict the flow through the valve. Good one for the memory bank! Thanks again....



   
ReplyQuote