looking for info about hydro elev. floor to floor time by code , anyone has a pdf explaining by travel and car speed ?
thnks
Certainly the code will cite any car running in excess of 10% more or less than rated speed (if checked), but that’s the only code reference I recall.
But…I could be wrong in the day and age in which we live. Nothing surprises me anymore no matter how ridiculous it may seem.
I would recommend downloading Kleemans Lift Tester App on an iPhone, it's free and very accurate. Use it to determine if your contract speed is what the elevator runs at full speed. I have tested that app on some 500 fpm cars and it's within 1-2 fpm.
I had a customer complain one time and said my elevator is supposed to be this speed, and these two floors are this far apart and the math says it should be x seconds but it's taking 10 seconds longer, it's not going fast enough. I had to explain acceleration, deceleration, leveling time..
I remember fighting with a traction car trying to get original floor to floor times for the consultants report. Realizing that preopening had been taken off years earlier, I put it back on for the customer to ride. After taking it for a trip the customer said “ put it back to normal and we’ll take care of the consultants”
I agree with others that sometimes it’s hard on the equipment and ride quality trying to shave off another second. For what?
As to how reliable it is or how they perform over time I don't know. Maybe one of these other guys has dealt with them more than I have. These consultants today are just ludicrous to deal with.
As to how reliable it is or how they perform over time I don't know. Maybe one of these other guys has dealt with them more than I have. These consultants today are just ludicrous to deal with.
nothing impressive is not the final solution and the encoder belt after couple of months of heavy elevator traffic start to create some issues
I have reports where they've measured everything in the green (up speed, door open, door close, etc) yet the performance time or floor to floor time is still unacceptable. How is that possible?
I also have report where they ding a 125fpm hydro for going 143fpm. Guess what speed I measured it at? Hint, it wasn't 143fpm
I could go on and on but what I would do if I were in your situation is ask building rep to ride the elevator with you and ask if they're happy with the ride. Then explain that the reports are nonsense and if they insist on making the changes explain it would likely lead to shortness of life for equipment.
side note: if you ever get a report for escalator it will always say auto oiler not working I guarantee it