Janus photo eye, gal movfr2 door operator.

Don’t have any door operation in full auto and doors start closing only when photoeye is blocked… any idea as to what could cause this?



   
Quote
(@Jcjphoenix)
Joined: 1 second ago
Posts: 0
 
Try swapping input board for close. You might have one for heavy doors which isn’t being used.



   
ReplyQuote
(@Indirtwetrust)
Joined: 1 second ago
Posts: 0
 
Sounds like your edge is wired backwards. N/O vs N/C contacts.



   
ReplyQuote
(@EElevator)
Joined: 1 second ago
Posts: 0
 
Dirt is right.

You can always try putting it in phase 2 to cut out the light curtain to rule it out



   
ReplyQuote
 MX4
(@MX4)
Joined: 1 second ago
Posts: 0
 
Originally Posted by Indirtwetrust
Sounds like your edge is wired backwards. N/O vs N/C contacts.

That is exactly what came to mind and willing to bet money on that being the problem.



   
ReplyQuote
(@Csalazar311)
Joined: 1 second ago
Posts: 0
Topic starter  
Easy fix! Was in N/O instead of N/C. Fixed it yesterday morning! Thanks for the help guys. Work safe



   
ReplyQuote