10/08/2013 9:55 am
Picked up a dover LMH 3 stop hydro on my route, never seen one before. Anyone have any experience with these?
10/08/2013 9:05 pm
If it has the plc I think they are a fairly decent controller. Parts for these are still available though vertical express or TKE I believe. If it is the earlier non PLC version your in trouble as far as parts and support.
11/08/2013 9:52 am
...I have been maintaining this equipment for awhile at present time I have 6 and they are all 5-stop freights w/peelle doors..have never encountered any problems with this equipment ..work horses..
Topic starter
12/08/2013 4:43 am
Well this is good news. There is some sort of service tool that was in the machine room. Hopefully ITS can send me some manuals soon.
03/11/2013 11:39 am
5 volt power supply for logic, and two main logic boards, a relay board and logic board, these baby's are expensive. The relay board has the field wiring terminals and can be found on the prints. It comes down to your control voltage, P24, being pulled to ground with the logic board to initiate a circuit. If you can get a manual, they have pin identification for signals on the chips and drivers. and a manual has a set of prints in it hopefully.
Last edited by mjm; 11/03/13 03:42 AM.
03/11/2013 10:47 pm
Sbrmilitia have your supervisor get on TNET there are LMH manuals on there
The tool is to program I/O information in the PLC and set parameters
That is explained in the manual
05/11/2013 10:15 am
The tool is a Idec programmer..have not had any eprom issues with this equipment..find it very reliable
Topic starter
06/11/2013 8:20 am
I got some info off of T net for it. Haven't had any issues with this car yet. This car runs constantly and only a few door calls. Next to my DMCs one of the better running cars I have on my route full of junk.
17/12/2013 8:30 am
Any one have board prints for a lmh . Have one that fire recall isnt working properly. when you run up on phase 2 and turn the key in car to normal car will not return to fire recall floor
Topic starter
17/12/2013 11:16 am
Board prints?
17/12/2013 11:33 am
Problem is in the software. Thats what the programmer is for. Changing the software without the program is not for the faint of heart. What version of software is in the controller? It will be printed on the program chip. Should be something like 8LILH. This means up to eight landings in line hydro. With the programmer, you can copy the program into another Ram pack and then experiment with the duplicate and not mess up the original programming.
17/12/2013 11:35 am
I said that the problem is in software, but I am assuming that all inputs are correct when you have this problem. Also, check your code date and see whether or not the code addressed this condition before you change anything.
17/12/2013 11:39 am
Originally Posted By: Johnny
I said that the problem is in software, but I am assuming that all inputs are correct when you have this problem. Also, check your code date and see whether or not the code addressed this condition before you change anything.
IDEC's you can download ladder logic, but no labels if you don't have the source code. In other words you download, look at a bunch of contacts, coils, timers, counters, but you have no clue what they do because you don't have any labels.... That is unless you have the source coded.
18/12/2013 9:26 am
I have the labels for certain LMH programs, thats why I ws asking which version he has.
05/01/2014 1:45 pm
Have the same problem on one of mine I have to run it down to recall floor before it will return to normal