I have a dmc that will not run up from 1st fl. you set car call the doors close and pump acts like it is bypassing, elevator goes no where and pump shuts down like its the low oil timer. it will run up and down on inspection. ran to 3rd/top floor. put in auto car leveled to 3rd. rode car to 2nd then to 1st. power was shut off, could I have lost programming



   
Quote
(@solidstate)
Prominent Member
Joined: 17 years ago
Posts: 643

   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759

   
ReplyQuote
(@silly)
Estimable Member
Joined: 17 years ago
Posts: 215
 
Doesn't the DMC run single coil in the up direction? Think it runs up fast only until slow coil is picked for slowdown, inspection is run on this up slow coil. My guess is bad UP fast solenoid or wiring to it.



   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759

   
ReplyQuote
(@philelevman)
Trusted Member
Joined: 17 years ago
Posts: 42
 
Check your switches on the side of the car. Can almost guarantee you have a broken wire in your up slowdown TSL I think.



   