24/07/2013 2:05 am
I have a SE input that does go low at the operator as indicated buy VOM and the LED on the operator board.
Im assuming this goes directly into the CLC.
Im assuming this goes directly into the CLC.
We have no door reversal. How would you correct?
Ive sold a Door Screen, but can I/O s be reassigned in the CLC with a FAST tool?
25/07/2013 7:48 am
..Questions did this elevator have the mechanical safety edges.as well as the dover lite rays..original?
25/07/2013 7:51 am
Just a thought, but try the EE terminals on the door op. board. It's been a while since I installed a screen on a DMC, but seem to remember having similar problems. You may have to jump out the SE terminals, to make it work correctly. Just going by my memory, which seems to be getting shorter by the day.
25/07/2013 8:53 am
that would be correct if you are doing away with the safety edges you need to get that SE input Hi..SE1-A to SE2-b..on the operator terminal strip...nc lite ray contacts fire EE between P24C and EE (
Topic starter
26/07/2013 3:25 am
Yes, OEM SE and photo eyes. Photo eyes do work so Im planning to install a door screen to the EE input.
was curious if these inputs fail do you need to change EEPROM and reset all parameters?
Topic starter
26/07/2013 3:28 am
Thanks Guys
26/07/2013 7:16 am
No, you should not have to reset CLC adjustments if the screen fails. We replace the battery on CLC board annually. It's a CR2430 battery located behind the COP on the CLC board. It's cheap insurance, if power goes out and battery is dead. No big deal to put CLC and door adjustments back in. A bit more involved of you have a tape selector. Also, no need to replace EPROM if inputs fail.
Last edited by Elevatorfella; 07/25/13 11:17 PM.
Topic starter
27/07/2013 9:51 am
Ya ive been been changing the batteries on the unit Ive acquired. Seems no one logs battery replacements. So do the inputs actually fail or ?
28/07/2013 2:57 am
Those batteries last a lot longer than you realize. As long as you have the parameters copied for easy setup, why bother?
Topic starter
28/07/2013 9:07 am
Ya I hear ya.
But what do you do if the I/O fails? Reset parameters?
25/08/2013 11:47 pm
Actually the SE input goes to the door board, and the door board takes care of reopening the doors. The door board sends the SE signal to the CLC through the communication line, so the CLC can handle timers and stuck devices and such. When then the CLC doesn't want the doors to open, it sends an inhibit signal to the door board(like when running up and down).
So if your edge is working good, and not reopening, then you probably have a bad door board(once lost the gate input on a door board, pretty rare).
All the comm line traffic can be seen on the door status 0,1 screen on your user tool.
Topic starter
05/09/2013 6:14 am
Thanks, Good info Tarth