TIDBIT On Swift Futura Cycling the car

3 Posts
2 Users
0 Reactions
2,872 Views
(@sbrmilitia)
Honorable Member
Joined: 17 years ago
Posts: 448
Topic starter   [#7762]
On a T-4 when you cycle a car you can set rsd=# to delay the next run sequence. Well on a Swift Futura after you set up your floors make sure to say yes to the top and bottom landing. Use CTD=# (call test delay) and it will delay the run sequence at the terminal landings. So you can cycle a car for days without burning it up. Its not in any of their books and the guy came down from CEC to speak with our building did not know anything about it.



   
Quote
(@e-man)
Honorable Member
Joined: 17 years ago
Posts: 480

   
ReplyQuote
(@sbrmilitia)
Honorable Member
Joined: 17 years ago
Posts: 448
Topic starter  
On some of the older Futura the software does not support this parameter. So when you type in CTD and it does not give you a value then no go.



   