Elevator Forum

Notifications
Clear all

330a help

12 Posts
1 Users
0 Reactions
10.1 K Views
(@beaupeep)
Joined: 1 second ago
Posts: 0
Topic starter   [#6017]
Had someone knock door off track. Put back on and have 202 fault. Doors will close but won't open. Do not have extra info code. Any ideas? Thanks



   
Quote
 jkh
(@jkh)
Joined: 1 second ago
Posts: 0
 
B
202 is a generic door code. Look through some of the earlier Schindler 330a posts. If you click on technical questions then click subject you can find everything listed as 330a and Schindler 330a.

Is there a smlcd on the controller?
Are you sure the car gate is fully closed?



   
ReplyQuote
(@beaupeep)
Joined: 1 second ago
Posts: 0
Topic starter  
Extra info code is 00000001



   
ReplyQuote
 jkh
(@jkh)
Joined: 1 second ago
Posts: 0
 
B
So if the doors will close but not open!
Is your close limit functioning properly?



   
ReplyQuote
(@beaupeep)
Joined: 1 second ago
Posts: 0
Topic starter  
Jkh, talked to another mech and he said could be door op board in cop could of fried after trying to open with door being knocked off, ever seen that



   
ReplyQuote
 jkh
(@jkh)
Joined: 1 second ago
Posts: 0
 
B
Anything is possible!
What have you checked so far?
Do you have prints?
Did you check your inputs for your limits?

Last edited by jkh; 02/28/13 02:15 AM.


   
ReplyQuote
(@E-man)
Joined: 1 second ago
Posts: 0
 
Use the test switch on the TDC board in the car station, that'll rule out the board.



   
ReplyQuote
(@billvator)
Joined: 1 second ago
Posts: 0
 
have you tried to kill power and shot the "cap"? make sure the doors are closed when you boot back up let them do a learn run



   
ReplyQuote
 PGL
(@PGL)
Joined: 1 second ago
Posts: 0
 
extra info 01=KET-Oand KET-s are active at the same time did an open or close limit get damaged?



   
ReplyQuote
(@beaupeep)
Joined: 1 second ago
Posts: 0
Topic starter  
E-man, tried from tdc board to open but wouldn't work but still closes. We sent the board in for repair. Are any of the pots on the bottom of board for current limiting? Thanks for extra info pgl



   
ReplyQuote
(@E-man)
Joined: 1 second ago
Posts: 0
 
Is the OL a proximity switch?



   
ReplyQuote
(@beaupeep)
Joined: 1 second ago
Posts: 0
Topic starter  
Thanlks for help guys, ended up replacing ol proxy. Is there any write up for the pots at bottom of tdc board or adjustment procedure for door op.



   
ReplyQuote
Share:
Scroll to Top