Lookin for some input or paperwork for a erl Westinghouse 74 vintage. Elevator runs too fast. Trying to figure what makes the voltage stops increasing once it gets to speed



   
Quote
(@e-man)
Honorable Member
Joined: 17 years ago
Posts: 480

   
ReplyQuote
(@john-jay)
Prominent Member
Joined: 17 years ago
Posts: 798

   
ReplyQuote
 Boa
(@boa)
Estimable Member
Joined: 17 years ago
Posts: 141
 
Not sure if this helps. On the older versions of the ERL controllers low insulation resistances to ground on the main loop circuits could cause overspeeding in one direction and not being able to properly compound



   
ReplyQuote
(@vatorgator)
Honorable Member
Joined: 17 years ago
Posts: 432

   
ReplyQuote
(@ceege)
Eminent Member
Joined: 17 years ago
Posts: 15
Topic starter  
Tried adjusting hs pot and nothing, I'm gettin over speed in both directions, but what's weird is it randomly worked absolutely perfect for like two hours and right before I was going to turn it loose it permanently crapped out. We've had this on contract for five years and it never ran that good, don't know if that throws any other signs up. Thanks guy



   
ReplyQuote
(@rolly)
Honorable Member
Joined: 17 years ago
Posts: 729
 
If the HS pot does not change anything you could have a Motor Field problem or a bad SCR or circuit Board Controlling Generator Field. Have you checked Standing, running, & forcing voltages? If you have more then one car, check and compare the Ohms in Motor Fields. Have you checked with a Tachometer how fast it is really going? Make sure you have no grounds in Loop Circuit.



   
ReplyQuote
(@b69t69)
Active Member
Joined: 17 years ago
Posts: 8
 
Sounds like it might be shored look circuit to me look for shorted brush rigging's be be 10 meg of higher to ground.



   
ReplyQuote
(@uppo72)
Honorable Member
Joined: 17 years ago
Posts: 562
 
Originally Posted By: Rolly
If the HS pot does not change anything you could have a Motor Field problem or a bad SCR or circuit Board Controlling Generator Field. Have you checked Standing, running, & forcing voltages? If you have more then one car, check and compare the Ohms in Motor Fields. Have you checked with a Tachometer how fast it is really going? Make sure you have no grounds in Loop Circuit.

Hey Rolly, what do you mean by forcing voltages? Which area?



   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759

   
ReplyQuote
(@e-man)
Honorable Member
Joined: 17 years ago
Posts: 480

   
ReplyQuote
(@uppo72)
Honorable Member
Joined: 17 years ago
Posts: 562
 
Originally Posted By: Indirtwetrust
He's talking about the motor field voltage/current. Forcing is full field.

Ah ok I understand now. I only ask as I haven't come across anyone in our parts who call it this, but just call it the pattern circuit s curve and loop circuit build up.



   