Elevator Forum

Westinghouse Proble...
 
Notifications
Clear all

Westinghouse Problem

7 Posts
5 Users
0 Reactions
8,699 Views
(@newmech)
Estimable Member
Joined: 17 years ago
Posts: 203
Topic starter   [#19091]
Having trouble with an old 8 stop Westinghouse unit recently added to my route. I am not familiar with Westinghouse equipment model names or prints or anything for that matter. I do not have job specific prints. The controller has a monkey on a stick selector in the controller and very large coils on the car top leveling unit.

I found the car with the doors cycling, not making full close. Detector edge (Lambda III-D) checks out ok, door operator is an AT-400 with a relay interface. After powering down and checking relay contacts, locks etc. the problem appeared to be gone. I ran the car around and everything was looking good. I went to the machine room to pick up my tools and found door relays cycling.

The problem only happens when more than one call is latched. For example: if I place a car call to 4 and a hall call is latched for 5, the car will stop at four, 304 will drop and then the doors begin to cycle. If I manually reset 501, the doors will close and then I can latch another call. This scenario happens with any combination of hall calls or car calls at all floors. The car will run fine if calls are latched one at a time and another call cannot be latched until the doors are closed.



   
Quote
 jkh
(@jkh)
Prominent Member
Joined: 17 years ago
Posts: 904
 
NewMech,
Westinghouse usually has a data plate on the controller. By your brief description it may say something like a 2BC-ERL. You may also find the model number at the top of a page from your print. If you can't find a data plate post a picture.

I would start by disconnecting the hall call if you can. Then work back from your door open relay circuit. If 44(?) is your door open, what is signaling for 44 to energize.

Once we know what you are working with things will go faster.

I still have some of my old info. If you PM your email address I will send you something to help familiarize you with Westinghouse.



   
ReplyQuote
(@rolly)
Honorable Member
Joined: 17 years ago
Posts: 729

   
ReplyQuote
(@e-man)
Honorable Member
Joined: 17 years ago
Posts: 480
 
DMR isn't a "monkey on a stick". DMR has chains.

I would say REL or ERL. If you have no knowledge or literature about Westinghouse it will be tuff. Make sure 438 and 42 is working correctly to start with.



   
ReplyQuote
(@rolly)
Honorable Member
Joined: 17 years ago
Posts: 729

   
ReplyQuote
(@newmech)
Estimable Member
Joined: 17 years ago
Posts: 203
Topic starter  
Controller type appears to be 2B C4-ERL 3. Someone else looked at the job last night and the problem cleared......he doesn't know how or why. I ran the car for about an hour this morning, it hiccuped once, too fast for me to catch anything.

I poked around a bit more and found a few contacts jumped and a couple of relays blocked, I hate Crap like this. I found some ERL prints, when the problem comes back I'll be a little more prepared. I also spoke with the former route mechanic, no longer at our company, this problem is not new. The problem apparently comes and goes, usually solved by jacking the mainline.



   
ReplyQuote
(@halfpick)
Reputable Member
Joined: 17 years ago
Posts: 239
 
I would suspect you have grounds in the system. Next time see what position the other car is in when this happens? Also always check for "half-pick" senarios on all relays!



   
ReplyQuote
Share: