Tac22 Car Call issue

12 Posts
1 Users
0 Reactions
10.3 K Views
(@solidstate)
Joined: 1 second ago
Posts: 0
Topic starter   [#27902]
Hall calls work as normal. Car calls answer the call, when car arrives at desired floor, door does not open automatically, have to press D.O.B. or the floor call again. Checked all magnets, parameters, inputs etc. Reloaded software also. Same thing.



   
Quote
 TC7
(@TC7)
Joined: 1 second ago
Posts: 0
 
Are you absolutely sure car is not overshooting and leveling back down?. I had this happen to me on Tac 32 hydro , didn't cause faults. I can't recall if it was only car calls that didn't open door, or car and hall.



   
ReplyQuote
(@solidstate)
Joined: 1 second ago
Posts: 0
Topic starter  
Yes we are sure of that have watched i/so and of course we are in machine room injecting calls and know that it is not overshooting



   
ReplyQuote
(@elmcannic)
Joined: 1 second ago
Posts: 0
 
Sounds crazy familiar. Turn it onto Fire Service, then off, and see if that clears it.



   
ReplyQuote
(@Al Carlson jr.)
Joined: 1 second ago
Posts: 0
 
Turn D32=2 , sounds like it 0 right now



   
ReplyQuote
(@Tweeker)
Joined: 1 second ago
Posts: 0
 
What type of door operator are you using?



   
ReplyQuote
(@solidstate)
Joined: 1 second ago
Posts: 0
Topic starter  
We were able to get back to the job this week. Tried Phase one and Phase two, still same issue. D32 was on 0, we changed that to 2 and wrt with a reboot. Still same thing. Speed of this job is 125fpm, and speed is fine.



   
ReplyQuote
(@Rolly)
Joined: 1 second ago
Posts: 0
 
Is there any faults in car with IMS? Also check group.



   
ReplyQuote
(@Elevtech23)
Joined: 1 second ago
Posts: 0
 
make sure d26=0



   
ReplyQuote
(@Rolly)
Joined: 1 second ago
Posts: 0
 
Might not be a bad idea to change D26=1 then change back to D26=0 since you loaded new software into board. Since you had D32 at 0 no telling what could be wrong. possibly a glitch when loading.



   
ReplyQuote
(@solidstate)
Joined: 1 second ago
Posts: 0
Topic starter  
this may be premature......will know for sure after Thanksgiving. It appears to be the expansion board. We are getting in the 24 volts, but at test points only 16 volts, with all the cons unplugged.

More to follow.



   
ReplyQuote
(@solidstate)
Joined: 1 second ago
Posts: 0
Topic starter  
We hooked up the new expansion board and the same thing. Thyssen thinks bad board, and are sending another one. We will bench test the next one before we hook up and then test afterwards. Keep it updated as we find out more.



   
ReplyQuote