Tac20

4 Posts
1 Users
0 Reactions
3,622 Views
(@chicago)
Joined: 1 second ago
Posts: 0
Topic starter   [#18048]
Getting 1041 fault. TAC20
???don't remember this one..



   
Quote
(@xxXBlazeXxx)
Joined: 1 second ago
Posts: 0
 
Door WatchDog closing failure � DCL input did not activate in expected time interval.
S Verify D21 and/or D22 adjustments

Last edited by xxXBlazeXxx; 09/19/16 10:29 PM.


   
ReplyQuote
(@elmcannic)
Joined: 1 second ago
Posts: 0
 
Chicago-
Be sure to check the door motor brushes.
Closing torque
Close start settings
Dragging gib
Too slow a manual close setting
Marginal DCL input
Soft spot on the primary door belt right near full close
New belts= excess drag on motor= 1041
Be sure you don't have a door ramp preventing full door closure
Or---
If it uses that magnet on the header for DCL, that may be a culprit as well.

Be sure to let us know what you found to remedy your trouble



   
ReplyQuote
(@chicago)
Joined: 1 second ago
Posts: 0
Topic starter  
Elmcannic,
nice tips. I will be back to job friday. Will check your ideas.
Thanks



   
ReplyQuote