12/08/2017 1:20 am
Hey guys working on a Tac50 currently on shutdown. Showing a 152 fault. Any experience with this one as its a B44 only. Thanks in advance.
Topic starter
12/08/2017 2:55 am
It helps to have the right generation of manual for the controller. Turns out 152 is an excessive drive temp fault. Either dtok or fan input failure.
12/08/2017 6:42 am
Ya that's a problem. They just re-assigned fault codes for new equipment. I keep the most current help files in IMS and the old one on my desktop. I would make sure the fans are working and replace the PMI module.