Just got a new bldg with tac50s. The car runs fine on inspection in the down, but in the up it shuts down after 1 run with a 1547 bslm. Brake swts look fine. Not sure if it's a tach issue since it's directional. My faults on my service tool doest have 1547. I don't have any manuals or fault log books. Any idea guys?



   
Quote
(@rolly)
Honorable Member
Joined: 17 years ago
Posts: 729

   
ReplyQuote
(@dj-411)
Eminent Member
Joined: 17 years ago
Posts: 32

   
ReplyQuote
(@dj-411)
Eminent Member
Joined: 17 years ago
Posts: 32

   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
The brake switch inputs are susceptible to noise. They should be in shielded cable with the shield grounded on 1 end. You can also wire a resistor from the inputs to P24 to keep them honest. What kind of machines are you working with?



   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759

   
ReplyQuote
(@dj-411)
Eminent Member
Joined: 17 years ago
Posts: 32

   
ReplyQuote
(@c-not)
New Member
Joined: 17 years ago
Posts: 3
 
U could have a roll back issue. If you have a 10k drive increase karb adjustment on the drive to limit rollback on your start



   
ReplyQuote
(@dj-411)
Eminent Member
Joined: 17 years ago
Posts: 32
Topic starter  
Thank you for good info. Is there a pick sequence that the process of looks at, like balm needs to pick before bake or has to drop out first? I get run monitor faults if the brake switch are a touch out of wack.



   