Tac 32. Fault 1110

29 Posts
9 Users
0 Reactions
21.2 K Views
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776
Topic starter   [#31210]
Hey guys. Got a Tac 32 shuts down once and a while on a 1110 fault
Only info in my manual is
1110. A17/b44 shutdown code. Inspection to reset.

Anybody have any other info ?



   
Quote
 KSNY
(@ksny)
Estimable Member
Joined: 17 years ago
Posts: 148
 
Isn't that door lock monitoring? The doors closed but not the gate switch, DCL or the order at which they are suppose to be made up is not correct. If I remember correctly, its Interlock, gate switch then door close limit. It is probably the plastic DCL sensor to far away from the magnet pickup. Could also be something in the saddle keeping the hatch door open while the Gate switch and DCL are made.



   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776
Topic starter  
This keeps happening intermittently... I can not find the DCL actuators
Is there any way to disable door lock monitoring on the controller Interface

Last edited by Jluff; 07/19/21 04:28 PM.


   
ReplyQuote
(@boomer)
Estimable Member
Joined: 17 years ago
Posts: 117
 
Check the cam and roller that retracts the small arm of the clutch. A lot of times this is cranked all the way back and it causes the doors to bind in the last 1/2” of the doors closing. Make sure the roller isn’t binding or wedging on the cam.



   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776
Topic starter  
There is no magnets for DCL and DOL. it’s an encoder.
Cam looks ok.
Keeps shutting down once a week on bottom terminal landing.



   
ReplyQuote
(@unkindbuffalo)
Trusted Member
Joined: 17 years ago
Posts: 44

   
ReplyQuote
(@solidstate)
Prominent Member
Joined: 17 years ago
Posts: 643
 
There should be DCL and DOL. Check you gate hanger rollers and you will see the magnets. The cigar switches are at the either end of the travel for the door. If all else fails, get the print for the door operator and trace down that con.



   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776
Topic starter  
Thanks. I will check for that. I can’t find these things yet. But I didn’t look on the gate hanger rollers



   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776
Topic starter  
No dcl n dol cigars on car door hangers. This is a LD-03 door operator with a 6300pa6 door board. It talks about dcl actuators on door operator cover but I can not find them.



   
ReplyQuote
 Goat
(@goat)
Estimable Member
Joined: 17 years ago
Posts: 114
 
Is that the only fault logged? I had one that had that fault with quite a few others. Ended up being the magnets on back side of the selector tape got moved and when it did its jack resynch it would shut down. For some reason it would also give me the 1110 fault.



   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776
Topic starter  
Yes that is only fault I’m finding. But it’s always in the basement when I find it. So maybe you are right. I will check My back side magnets. If I remember correctly. You shoukd feel for gaps and close them



   
ReplyQuote
(@elmcannic)
Honorable Member
Joined: 17 years ago
Posts: 635
 
IIRC there is a parameter setting for that B44 shutdown code. Set to “0” or deselect it to not have it in play. If your problem persists at the basement only, after you’ve checked magnets (if you do find the notorious non glued magnets) be sure to apply silicone to one edge of each slipped magnet, or a few drops of gorilla glue to three points after they’ve been situated properly AND tested.
Back to what KSNY was saying. Be sure the sequence of CG, DCL, DG signals are tight. Could be a bouncy pecker or the shorting bar is riding up and off the two contacts due to too much travel into the interlock box (or conversely too tight interlock and the pecker isn’t dropping right away). And again if I remember correctly, B44 shutdown can occur during the open cycle as well. As far as the signal sequence goes, my memory is different than KS, so maybe IDWT can chime in to clarify.



   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
LD-03 DOL, DCL. sensors in header, magnets on hanger connecting bracket. Item 14, 15, 16.
Attachments
Screen Shot 2021-07-28 at 5.48.48 PM.png (260.97 KB, 50 downloads)



   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776
Topic starter  
Thanks dirt. Can Adjustment 025 be changed with UIT on controller ?

Last edited by Jluff; 07/29/21 01:18 AM.


   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759

   
ReplyQuote
Page 1 / 2