Elevator Forum

Notifications
Clear all

Tac 20 Parking

7 Posts
4 Users
0 Reactions
5,414 Views
(@solidstate)
Prominent Member
Joined: 17 years ago
Posts: 643
Topic starter   [#29695]
Is there a parameter to keep the doors open on a tac20 after it has reached a floor, but close when a hall call or car call is entered?

Have a university that wants to have the doors open to increase air flow with the pandemic going around.



   
Quote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
Thyssen calls it Next Up operation. This should work but if you can wait til tomorrow I can try it in a simulator. Group parameters: LER = 1, LBY = parking floor, and set CSW bit 14.

Last edited by Indirtwetrust; 07/28/20 09:52 PM.


   
ReplyQuote
(@rolly)
Honorable Member
Joined: 17 years ago
Posts: 729

   
ReplyQuote
(@solidstate)
Prominent Member
Joined: 17 years ago
Posts: 643

   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
Okay, lots of caveats with Next -Up on the TAC20. It works just like I suspect you want on a TAC50-04. Waits at the parking floor with doors open until a car or hall call is placed, has to be the parking floor though.

On the TAC20 what I said yesterday was correct, LBY and LER is just how you enable parking, then set CSW-14. Car will park, then open doors for 8 seconds, then Next-Up turns off and doors close. You can change the time with NDH but only from 3-30 seconds. You’ll find though, that when you place a car call the doors still stay open for NDH time. NCO defaults to 3 so you have to put in 4 car calls to override Next-Up. You can set NCO to 0 which makes it take the car call immediately but it will not bypass Next-Up for hall calls so it will sit there until NDH time expires before answering the hall call. Maybe okay for a duplex but not for a simplex.

I should have asked how many cars are in the group.



   
ReplyQuote
(@solidstate)
Prominent Member
Joined: 17 years ago
Posts: 643
Topic starter  
Thanks for the help.

There is 8 different buildings and of course they are all simplex.

We tried the above today, and works just like you say. So it appears that we can not keep the doors open for air flow purposes, until a hall or car call is entered.



   
ReplyQuote
(@johnny)
Honorable Member
Joined: 17 years ago
Posts: 473

   
ReplyQuote
Share:
Scroll to Top