Tac 20 in low speed

5 Posts
2 Users
0 Reactions
4,101 Views
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776
Topic starter   [#18584]
Hey guys. I got a Tac 20 stuck in low speed in the up direction. The coil isn't being energized. It goes to the 2nd floor (top floor ) in low speed whole way up. Does any body have any advice ? Txs



   
Quote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759

   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
You need to see if VC4A and VC4B relays are picking (K7 & K8 on 188E.) If they are not, you will need IMS to see if they are both going high on the I/O map. If they are both picked you should have 120vac at con 16 pin 8 to ground, if not there is a bad N/O contact on one of the 2 relays. If you still don't have 120vac to the CNWI board con18 pin 7-8 then TSL2 relay is not picked or has a bad contact, if no 24vac to TSL2 coil you have a selector problem and should have other faults. If you do have 120vac at the CNWI board con 18 pin 7-8 but don't have 120 vac out of the CNWI con 17 pins 7-8 the CNWI board is bad.



   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776
Topic starter  
I do have ims. Just not that great at using it. I'm pretty sure those relays are not picking. I will check that info. Thanks a lot.



   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
If both those fast I/Os are not going High and the slow ones are, I once saw that happen because the door zone magnet had moved so make sure DZ1 and DZ2 inputs are high and DZ1M and DZ2M are low when at the floor. You could have a NTS problem but you should be getting a 1062 every time it runs up.



   
ReplyQuote