Elevator Forum

Tac 20 hoistway sca...
 
Notifications
Clear all

Tac 20 hoistway scan not completing in ims

4 Posts
3 Users
0 Reactions
3,745 Views
(@getemup)
Eminent Member
Joined: 17 years ago
Posts: 22
Topic starter   [#21098]
Working on a tac 20 and it is not completing hoistway scan in Ims, any suggestions as to why that may be? But unit is still running. Thanks



   
Quote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
How far does it get? When the scan window is open, it should say Pass, Pass, then Fail at some point. What point? UNL is the last thing it needs to see.



   
ReplyQuote
(@elmcannic)
Honorable Member
Joined: 17 years ago
Posts: 635
 
If you're trying to do a scan, there must be a reason. Or, are you just trying to learn a bit more about this control?

On the scan, at what point does it fail? The scan window should tell you.
If your having an intermittent fault, run the recorder also in IMS while running the car, and just maybe you'll catch it while you're there. Check the slowdown magnets for any gaps and correct.
Also, post the faults if you're lacking documentation.
DZ and DZE (and magnets gaps) are common selector faults that can be annoying and intermittent.



   
ReplyQuote
(@getemup)
Eminent Member
Joined: 17 years ago
Posts: 22

   
ReplyQuote
Share:
Scroll to Top