Elevator Forum

Notifications
Clear all

Tac 20. 1086 code

6 Posts
2 Users
0 Reactions
2,144 Views
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776
Topic starter   [#33294]
Getting riders trapped on top terminal landing. Seems to be 1086 Normal terminal slowdown limit failure sensor or magnet failure of NTST, NTSB, TSL1, TSL2 It is very intermittent

-Invalid configuration or adjustment of magnets or sensors
-Corrupted memory
-Bad CPU CARD

All magnets seem fine. No gaps on back side of tape magnets.
Has anyone seen a bad selector board cause this ?

Also car relevels every 2 mins sometimes. But passes standing test ..no sinking with power off

Last edited by Jluff; 06/23/22 03:08 PM.


   
Quote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776

   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
First thing, I’d do several NTS tests to make sure that is working correctly. You should get a 1062 and the car does an NTS stop and keeps running. The 1086 is ETS, what you get when NTS fails. The ETS sensors are on the Auxiliary Sensor card (back selector board.) I suspect a failure of that board could cause this. Or the ETS/NTS signals getting back to the controller through travel cable wires or the CWI board in the car.



   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776

   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759

   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776

   
ReplyQuote
Share: