Got a 2 stop Tac 20 that goes up in low speed and logs a 1062 and 981 fault. My magnets seem perfect. I took selector apart and don't see anything wrong ... Is the selector board bad?



   
Quote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
Does NTST never go high? I believe when you are away from the top slowdown magnets, you should have G24 at con3-4 on 188e. If you don't, trace it back to NTST travel cable #22 to CWI board con 400-6 to 400-6 on selector. If you are out of the slowdown mags and have no G24 on selector con400-6, but do have G24 coming in to selector on con400-2, you probably have a bad selector board. I would guess the sensor on the aux sensor board but it goes through the main sensor board too. And if NTST does not change state in IMS when conn3-4 is grounded, 188e input is bad. You can move it to a spare input.



   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776

   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759

   
ReplyQuote
(@elmcannic)
Honorable Member
Joined: 17 years ago
Posts: 635
 
You mention checking the magnets and they look fine. But... It doesn't take but maybe 1/16" gap between any two magnets and your description of slow speed up is what your gonna get.
It's easily overlooked at the bottom because you can't twist the tape around like the top to view it.

On moving I/O's, I believe the field CONN wire as well as the I/O need to be changed to that spare location.
If your using IMS you can record the up run, play it back and see which inputs are dropping out at the improper time.



   
ReplyQuote