TA50-04 Run Monitor

9 Posts
2 Users
0 Reactions
4,320 Views
(@wltr00)
Honorable Member
Joined: 17 years ago
Posts: 359

   
Quote
(@wltr00)
Honorable Member
Joined: 17 years ago
Posts: 359

   
ReplyQuote
(@wltr00)
Honorable Member
Joined: 17 years ago
Posts: 359

   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759

   
ReplyQuote
(@wltr00)
Honorable Member
Joined: 17 years ago
Posts: 359
Topic starter  
RRF, SFR & TFR no effect. DZ IO's are all active again and some IO's in the car section of the IO map don't agree with car IO's on a running car in the same group.



   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
With a DCN command is the Main COP online? Make sure the J16 parameter is not a 0, should be the same as the other car. What are you getting for faults?



   
ReplyQuote
(@wltr00)
Honorable Member
Joined: 17 years ago
Posts: 359
Topic starter  
DCN looks good...everything is online. J16 is good. Faults are 1525 & 1863. DHNF also shows everything is online in HW.



   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
Hmm. Is this an MRL? Do you have an SRS Input? It’s the slack rope switch. It wires to the bottom HN card, could be open or a problem with that HN. When you typed in DHNF, did it say anything about a blown fuse before displaying the HN table?



   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759

   
ReplyQuote