T3 CD Issue

4 Posts
4 Users
0 Reactions
2,035 Views
(@wltr00)
Honorable Member
Joined: 17 years ago
Posts: 359
Topic starter   [#26596]
I'm having a close door issue with a T3.

The attached photo shows my CD output is active, but I am not measuring 120VAC on P11 of the CD output IO. I have changed the PMI module and still no output. I have 120VAC on the P10 input to the CD IO. My doors are open and I cannot get them to close because I cannot activate the CD relay. If I jump 120VAC to to CD the relay energizes and the doors close.

Not sure what is going on here. Appreciate any help.

Attachments
Resized_20190416_092016.jpg (147.59 KB, 38 downloads)
Resized_20190416_110910.jpg (150.26 KB, 24 downloads)



   
Quote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
So you replaced PMI module 38 on PMI card #1? Did you check the Pico fuse for M38? That print doesn’t match your I/O map. Module 38 is P5-3 common, P5-19 output. Always go by the I/O map.