Triplex group. Upon arrival F-3 fuse was opened on Number one car, replaced it and opened it right away. Checked out power supply seemed ok, replaced fuse again, and all seemed good, except for no hall calls work, turn off number one and the other two work fine. If we take either side communication cable off of J 2 of CPU on #1, the other cars answer hall calls, and #1 car works as if on independent. Leaning to CPU card, but looking for other inputs,from people that are smarter than me.



   
Quote
(@solidstate)
Prominent Member
Joined: 17 years ago
Posts: 643

   
ReplyQuote
(@solidstate)
Prominent Member
Joined: 17 years ago
Posts: 643
Topic starter  
We got the board back and will install it. Looks like it have bad comm chips and IC sockets.

Will post results



   
ReplyQuote
 MX4
(@mx4)
Estimable Member
Joined: 17 years ago
Posts: 226

   
ReplyQuote
(@solidstate)
Prominent Member
Joined: 17 years ago
Posts: 643

   
ReplyQuote
(@solidstate)
Prominent Member
Joined: 17 years ago
Posts: 643
Topic starter  
I wish I was posting the resolve...but alas not our fortune today.

Our thinking was since its isolated to car one causing the issue with the hall calls, we could remove the traveling cable wires VL+ and V+ and start isolating it like that. With both of those removed feeding the car, it is still same issue.

I was going to try removing the module cards one at a time and try that. Any other ideas?



   
ReplyQuote
(@wltr00)
Honorable Member
Joined: 17 years ago
Posts: 359

   
ReplyQuote
(@solidstate)
Prominent Member
Joined: 17 years ago
Posts: 643
Topic starter  
My wish came true....we got it. Think the original problem was a module on the hall call module board. One of the techs started there and replaced the modules, put it all back in and then she wouldnt do anything. Pulled the board back out and went through again, car ran then but still no hall calls. So we sent CPU board to access for this issue and I posted what they said. Another tech went by today and....we had misplaced con P5 on that module board. Put it on correctly and we are good to move on to the next issue.

Thanks WLTR00 we have never tried a confidence test, will have to read up on that. I ASSUME that performs a self check of the modules?



   