TKE Endura MRL Hydro

1 Posts
1 Users
0 Reactions
828 Views
(@rejivijay)
Active Member
Joined: 17 years ago
Posts: 6
Topic starter   [#36574]
I have intermittent issue with TAC 32 Endura, after weekly generator tests. Elevator shutdown with Runmonitor faults 1673&1695.Unplugged the UPS and the issue being solved. I need to connect back the UPS. How can we fix this issue permanently. Are there any parameters to adjust. Appreciate your suggestions.



   