Swift meridia

4 Posts
1 Users
0 Reactions
2,989 Views
(@Local 84)
Joined: 1 second ago
Posts: 0
Topic starter   [#31689]
Hello everyone. Just replaced old HPV 900 drive with a new HPV 900 series 2 drive. Set the drive up per manual for closed loop system motor data is entered correctly speed of car etc. When I try to run on inspection brake picks but motor does not turn im reading 50v ac from the leads going to the motor from the drive. Is there a setting I’m missing? Any help is appreciated



   
Quote
(@UpandDown2321)
Joined: 1 second ago
Posts: 0
 
The new inputs are on different terminals check to be sure those are correct for the new configuration. Check the encoder as well I replaced these drives on a swift and the plug had to be removed and repinned. You can check the speed command as well on the drive and compare to the swift command as a start.



   
ReplyQuote
 KSNY
(@KSNY)
Joined: 1 second ago
Posts: 0
 
Did you do an "Auto-Tune"? If not that will need to be done first. The procedure should be in the book that came with the drive.



   
ReplyQuote
(@Turbo6)
Joined: 1 second ago
Posts: 0
 
Sounds like as said above your inputs are probably misconfigured. Sounds like your commanding drive on but not a direction.



   