Hey guys - kept getting F6 a-b-1-0 every few days - safety string is made up - all connections good . Replaced the sf1 and sf2 relays - M RELAY aux contacts and smartrise told us to replace the TOC SRU board which we did - And with my luck , still getting the F6 fault



   
Quote
(@jimbonj)
Estimable Member
Joined: 17 years ago
Posts: 67

   
ReplyQuote
(@elevatorguy619)
Eminent Member
Joined: 17 years ago
Posts: 28

   
ReplyQuote
(@jimbonj)
Estimable Member
Joined: 17 years ago
Posts: 67
Topic starter  
AC traction 2.43 - today at controller theee was 3 f49 drive faults then the F6 safety string open- hpv series 2 says encoder fault - maybe time for a new tach

Last edited by JimboNJ; 10/03/17 06:23 PM.


   
ReplyQuote
(@turbo6)
Estimable Member
Joined: 17 years ago
Posts: 118
 
Is this on a pm gearless? If so we just had similar issue and if your inertia is set to high it will cause this. Look and see what your estimated inertia is in the pit that number in for your inertia setting or a tad lower.



   