hi all working on schindler 3300,can not access error through menu 50
have tested the scpu to another lift and working okay,once you reset it goes
to the last floor opens the door and reigisters status 98.What could be the
problem
have tested the scpu to another lift and working okay,once you reset it goes
to the last floor opens the door and reigisters status 98.What could be the
problem
30/04/2020 3:44 pm
hi,
status 98: elevator is blocked folloving a fatal error
reset of fatal errors of control and inverter
how to solve:
1. on user interface choose10 and press OK , shows 101
2.press OK again to confirm submenu 101,, shows 101 0
3.change the value from 101 0 to 101 1, and press OK
4. leave the menu and press reset button on SCPU