Hi guys, had an 0445 fault level at the bottom landing. Reset and tested operation, car ran without any issues. What causes a 0445 fault?



   
Quote
(@notime)
Reputable Member
Joined: 17 years ago
Posts: 197
 
04 45:
E_DRIVE_TRIP_PREPARATION_FAILURE
The drive trip preparation was not successful due to logical data mismatch

C1:The car drive got invalid trip preparation data from the elevator control
(for example car load necessary to calculate pretorque out of range, or invalid trip profile)
A1:Check drive parameter.Check drive capability.Check load measurement

C2:Communication problem between elevator control and car drive
A2:Check data connection between elevator control and car drive

C3:Software problem (deadlock) at elevator control or at car drive
A3:Wait for successful recovery



   
ReplyQuote
(@beaupeep)
Honorable Member
Joined: 17 years ago
Posts: 316

   
ReplyQuote
(@beaupeep)
Honorable Member
Joined: 17 years ago
Posts: 316

   
ReplyQuote
(@buffered-out)
Active Member
Joined: 17 years ago
Posts: 6
 
Trip Profile Invalid
Pretorque out of range
Expected Drive inverter prep state not reached (software hang up)
NTSD monitor not set when required
Safety Circuit not closing at unknown location
Door Contacts (KTS, KTC) not closing during trip prep



   
ReplyQuote
(@beaupeep)
Honorable Member
Joined: 17 years ago
Posts: 316
Topic starter  
Thank you! So if extra info equals 0006, does that mean that door contacts not closing during trip prep?



   