I have a Schindler 300a that will not take a down call. After lowering the unit down within the bottom floor I can toggle back to auto and the unit will level in. Doors open, reach in give it a car call to 2 or 3, unit runs up. I walk up stairs, reach in give it a down call to 1, the doors close and the unit faults out. It’s lost.
I have verified my cigar switches, directionals, fuses, and relays are working according to the print. I do not have any means of communication to this board with software.
30/12/2022 10:04 pm
Fault Number ?
Topic starter
31/12/2022 6:08 am
This is an old 300a, no segment display of any kind.
31/12/2022 9:54 am
yes but hht show faults ans status
Topic starter
13/01/2023 5:48 am
I don’t understand, please explain
13/01/2023 7:21 am
No 300As had an SMLCD like the 330A. 300As are much closer to an MPH2 and require the same HHT tool for diagnostics. It looks like a DMC FAST Tool but there are some PC based programs floating around. It just uses RS232 with a 9-25 pin serial cable. I think ECI America still sells a handheld version that’s pretty nice too.