Otis MCS 120 Hyd. with Bucher

16 Posts
7 Users
0 Reactions
19.4 K Views
(@yus123)
Trusted Member
Joined: 17 years ago
Posts: 40
Topic starter   [#23859]
Dear All

I have a problem with MCS 120 Hydraulic with Bucher valve.
The lift very often has a problem with fault log DBSS only with status fault on Otis tool DAR ST.
Whenever has an error the call is not registered and will working Normal again after we reset the power supply OFF and ON.
We have changed the Bucher selenoid, the new LCB2 board. PSR switches, whole the contactors including LV1, LV2, and LVC.

Appreciate for your help. Thank in advance.

Attachments
ErrLog.JPG (43.79 KB, 43 downloads)



   
Quote
(@alex75)
Estimable Member
Joined: 17 years ago
Posts: 130
 
Hi Yus123

Does the lift have a pawl device?
If yes, try to disable the Anti Creep Device for testing purpose. Set parameter in LCB-II M1-3-1-4 (Drive parameters) ACD/UXT = 0 (Disabled).

/Alex

Last edited by Alex75; 04/26/18 06:48 PM.


   
ReplyQuote
(@yus123)
Trusted Member
Joined: 17 years ago
Posts: 40
Topic starter  
Hi Alex75,

We checked on site the parameter already disabled.
Since 3 years maintained the lift, we have changed Bucher selenoid valve 3 times already

Attachments
16_Drive.jpeg (281.57 KB, 39 downloads)



   
ReplyQuote
(@alex75)
Estimable Member
Joined: 17 years ago
Posts: 130
 
Hi Yus123

It looks like the only things that can generate the DAR state is:

- Fault from the Bucher control (Is the relay on the Bucher Power Supply connected?, If yes try to bridge this relay).
- Or one of these inputs have been active: OTS (Oil Temp Switch), PLS (Pressure Limit Switch), MPD (Motor Protection Device), THB (Thermo Contact).

/Alex

Last edited by Alex75; 04/30/18 07:00 AM.


   
ReplyQuote
(@yus123)
Trusted Member
Joined: 17 years ago
Posts: 40

   
ReplyQuote
(@pjalle)
New Member
Joined: 17 years ago
Posts: 1

   
ReplyQuote
(@yus123)
Trusted Member
Joined: 17 years ago
Posts: 40
Topic starter  
hello Pjalle,

I have not checked yet about the 0 value of Bucher Valve, could you advise me how to check this, please
I have checked the 0 value on parameter LCB_2 only.
the controller of the Bucher is Delcon Controller.



   
ReplyQuote
(@sampler)
Estimable Member
Joined: 17 years ago
Posts: 89
 
Dear Yus123, I have the same problem. Did you solve it. Can you help. Also Bucher 0-point has already been set and problems' going on.



   
ReplyQuote
(@heisenberg)
Reputable Member
Joined: 17 years ago
Posts: 280
 
Is there an error led showing on the Bucher delcon card when it faults?

Is it faulting during travel? Specifically in the down?
Do NOT touch the 0 point adjustment unless absolutely necessary.

You may need Bucher delcon hand tool to check Bucher system errors



   
ReplyQuote
(@sampler)
Estimable Member
Joined: 17 years ago
Posts: 89
 
The error occurs in the morning and always car at the bottom floor, not actived final switch but 12 cmm down.

hand tool errror: Warn: Bypass pr, Demand, problems keep on. thanks.



   
ReplyQuote
(@heisenberg)
Reputable Member
Joined: 17 years ago
Posts: 280

   
ReplyQuote
(@sampler)
Estimable Member
Joined: 17 years ago
Posts: 89
 
dear heisenberg, normally relevelling is working very well and many times tested. After hours, releveling may not occur due to cold oil or a valfe fail? So if I set parking floor for a diffrent floor samething may happen? But I tried floor changing to test.
As you say I set the parking floor "ARD-P and ARD-T". but controller malfunctioning. car goes for parking floor (screen turns ARD from IDL). then goes bottom floor (Service tool's screen shows PRK). again and again this keeps on. so I closed these parameters.



   
ReplyQuote
(@john-jay)
Prominent Member
Joined: 17 years ago
Posts: 798
 
Is there a tank heater? Or does this run the motor to heat the oil? If it runs the motor to heat, make sure the valve isn't moving the car when it is heating.



   
ReplyQuote
(@sampler)
Estimable Member
Joined: 17 years ago
Posts: 89
 
there is no heater. if oil temperature is the reason of this failure there's a reverse situation. Cause relevelling can not occur due to cold oil.



   
ReplyQuote
(@johnny)
Honorable Member
Joined: 17 years ago
Posts: 473

   
ReplyQuote