Need a Hand on a 211 if anyone can help that would be greatly appreciated. Car is now stuck on NAV mode. here is step by step what happened. doing a pressure test. once done was at the bottom floor, cycled power and after power up car is now stuck on NAV, (Not Available), Car was in operation before the test. there was no logged faults. spoke to a buddy of mine saying that some random times if power was shutoff while car was at bottom floor the car will get lost and to bring it to the middle of hoistway on inspection, reset and let the car find itself. this all seemed weird, as the no matter what floor zone i was in it would level into that floor and the PI would be correct. is there a way to get out of this mode. Not sure anyone has seen this specifically but any help would be awesome. Do have the Blue tool. Went through pretty much everything but im still reading through manuals to see if i missed something.

thank you

Jdiggiddy



   
Quote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
You do have safe right? C LED is lit. They will say NAV with safe open. Like if the stop switch gets flipped on the IOBD.
And not sure if the car would say NAV but I’d make sure there isn’t a conflict of inspection inputs like TCIC, TCI, IIS, MIS.

Last edited by Indirtwetrust; 04/30/21 06:32 PM.


   
ReplyQuote
(@beaupeep)
Honorable Member
Joined: 17 years ago
Posts: 316
 
This may sound dumb, but is it a soft start or contactors? I once had the overload trip while doing this and it threw me off.

Last edited by beaupeep; 04/30/21 08:01 PM.


   
ReplyQuote
 TC7
(@tc7)
Trusted Member
Joined: 17 years ago
Posts: 71
 
I have been hearing about more instances of Otis equipment losing eeprom . On 211 it's the chip that holds parameters, U26. If you rule out normal elevator problems, it may be a bad memory location on chip.

If this is the case you will have to get a chip burner, and possibly making copy of a similar working elevator, check all parameters, etc.



   
ReplyQuote
(@chrish2019)
Active Member
Joined: 17 years ago
Posts: 6

   
ReplyQuote
(@dripcan)
Estimable Member
Joined: 17 years ago
Posts: 131

   
ReplyQuote
(@smithereens)
New Member
Joined: 17 years ago
Posts: 2
 
What was the resolution of this? I am having this issue right now. Can run all day on inspection but says NAV on normal. My OCSS status is NAV but my MCSS status is IDL. Fuses are good, safety circuit is good.

Last edited by smithereens; 03/07/24 12:27 AM.


   
ReplyQuote
(@boomer)
Estimable Member
Joined: 17 years ago
Posts: 117

   
ReplyQuote
(@smithereens)
New Member
Joined: 17 years ago
Posts: 2
 
Yes iv cleared both pf and sac ram multiple times and done clro clr1 clr2 clears.
The only time I get an error is if I stop at a floor on inspection I get an FLRP error. Iv changed the selector board and the IO board.



   