Otis 211 needs ram cleared after FEO

2 Posts
2 Users
0 Reactions
1,433 Views
(@ryeguy)
Trusted Member
Joined: 17 years ago
Posts: 45
Topic starter   [#37507]
Is this a known issue with these controllers? I have a few jobs that require the RAM to be cleared to reset the car off fire service.



   
Quote
(@bowtiedrooster16)
Reputable Member
Joined: 17 years ago
Posts: 279
 
I have had a bank of 411s have that issue where you have to do M-1-5-1 to clear ram to reset fire service. I think we ended up replacing the key switch but I don't remember if that was the culprit cuz it was so long ago



   