More information please...
Suggestions were provided to your original post. Which have you tested, and do you have the MCE manual for this job?
When running on Independent Service, do the doors operate at all?
“5 elevator motion control”...meaning 5 elevators in group? Do you have a “Common Panel” to control dispatching? Or 5 landings/stops for 1 elevator?
You can also call MCE for troubleshooting help. Provide the “job serial number” on the silver sticker in the upper right section (typically) of the controller panel.
Already I was contact to Mce but is not proper response. I have a manual but I was checked in the manual . I couldn’t get.
Whether we are the in front of swing panel. When we are facing this problem that time in the swing panel showed normal operation.
At the same time in the Group Superviser panel monitor also normal . There is no fault.
I was opening the F3 menu. There is no error at the time of issue .
So please help me friends.
I PM’d this guy asking for answers to my questions (to not bore the forum) and didnt get the response i would expect.
You might be onto something.
Does problem occurred at the same area, both directions?
Does car run normal on 2 floor runs, what about 3 floor ?
On PTC can you confirm the STU and STD sensor change states?
DOF is on address 22 6th output from the right.
are you seeing the count change while the car moves? or is it lost and levelling into each floor?
check your LU and LD, are you stuck levelling?
are you getting STP, and is your F3 screen showing the car moving?
is your PI board showing the proper floors?
I gave you the ID, Label suggestion back on Feb 20. when you originally jumped in on the other MCE thread. Man...I coulda been the hero if you’d only read and understood the post.