Elevator Forum

Motion control MDZL...
 
Notifications
Clear all

Motion control MDZLV input failure

5 Posts
1 Users
0 Reactions
3,185 Views
(@Kcmprize)
Joined: 1 second ago
Posts: 0
Topic starter   [#36269]
Has anybody encountered MDZLV INPUT failure on Motion Control 2000 green board. Replaced selector board because it was discolored and burned on back side. Still faulting out after board change out. My next step is to change out HC-CTL board. Anybody have this issue before? Thanks for any input.



   
Quote
(@Indirtwetrust)
Joined: 1 second ago
Posts: 0
 
Pretty sure a bad DZ relay on the HC-CTL will cause that.



   
ReplyQuote
(@Kcmprize)
Joined: 1 second ago
Posts: 0
Topic starter  
Yes I changed out DZ relay, still same fault. Thanks for your input



   
ReplyQuote
 Dano
(@Dano)
Joined: 1 second ago
Posts: 0
 
Whats the leveling system? If it's an Edge, I would check the connection in the controller DZF (or DZR if it's a front and back car) as well as the car connections at the LSI board, DZF_M and DZR_M, make sure they are properly terminated.

At the same time reseat your RJ45 connector(s) at your tape head and at the LSI board. Beyond that you may have a board failure.

Same goes for the QUTE system, if that's what you have on that job, just the terminals change nomeclature accordingly.



   
ReplyQuote
(@Kcmprize)
Joined: 1 second ago
Posts: 0
Topic starter  
Replaced HC-CTL board resolved the problem. Thanks for input everyone.



   