Miprom 21 42 fault

8 Posts
3 Users
0 Reactions
6,017 Views
(@sbrmilitia)
Honorable Member
Joined: 17 years ago
Posts: 448

   
Quote
 jkh
(@jkh)
Prominent Member
Joined: 17 years ago
Posts: 904

   
ReplyQuote
(@sbrmilitia)
Honorable Member
Joined: 17 years ago
Posts: 448
Topic starter  
How do adjust it back? I watched the 90 percent switch go from low to high on my i/o and none of my motion averages were ? They all had values.



   
ReplyQuote
(@john-jay)
Prominent Member
Joined: 17 years ago
Posts: 798
 
Determine if the fault is at the top or bottom and adjust the mi + at the top or mi- at the bottom. The NTS board has pots to adjust voltages on rail sws. Put car on inspect and stop at each sw. Look at voltage and adjust accordingly. Meter goes on gan and mi + or - .



   
ReplyQuote
(@sbrmilitia)
Honorable Member
Joined: 17 years ago
Posts: 448
Topic starter  
Ive Changed the NTS board and set the voltages. +/- .8 +/- 4.3 +/-6.4 and +/-8.4 They are spot on.

But this fault seems to be caused by the ETS board. It isnt a fatal fault but I want to adjust it out.



   
ReplyQuote
 jkh
(@jkh)
Prominent Member
Joined: 17 years ago
Posts: 904

   
ReplyQuote
(@john-jay)
Prominent Member
Joined: 17 years ago
Posts: 798
 
the 42 is generated when the cpu sees the 90% speed sw. on the ets bd. out of tolerance. this happens on acceleration. there are a number of small speed bds. plugged into the ets bd. there is a pot on top of each bd. basically you look at motion averages to see when the 90% relay picked and adjust the pot. If I remember correctly counter clockwise makes the board pick at a higher speed. so at 90% of contract you should pick the relay. Also the fault can be generated by a faulty position encoder, or encoder coupling.



   
ReplyQuote
(@sbrmilitia)
Honorable Member
Joined: 17 years ago
Posts: 448

   
ReplyQuote