Having problems with velocity comparator and can’t learn hoistway. Tach and encoder are good , I have tach feedback pot all the way counterclockwise on allen bradly analog dc drive. I’ve got some info but nothing on calibrating pots on MSU board. I can’t try adjusting VC to 8v at contact speed because I can’t get it up to speed. Does anyone have info on MSU board adjustment and /or MSU bypass



   
Quote
(@rolly)
Honorable Member
Joined: 17 years ago
Posts: 729
 
All that info is in the black book with very good instructions. If you don't have a black book you should not be taking care of Miprom. It is essential to have one.



   
ReplyQuote
(@jcjphoenix)
Reputable Member
Joined: 17 years ago
Posts: 239
Topic starter  
Don’t have one. I’ve got the manual put out by Dover for miproms and that has gotten me by so far. Anyone have a pdf version of the black book?



   
ReplyQuote
(@workingclass)
Trusted Member
Joined: 17 years ago
Posts: 61

   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
The ITS manual has the MSU setup too. It’s actually quite good. But you should have the black book. I’ll PM you.



   