What controls the generator time out?



   
Quote
(@E-man)
Joined: 1 second ago
Posts: 0
 
Gosh, I don't work on new stuff 🤪
G39, MGT on the old stuff. Wouldn't it be in the HHT under Profile - Adjust?



   
ReplyQuote
(@Broke_Sheave)
Joined: 1 second ago
Posts: 0
 
Originally Posted By: E-man
Gosh, I don't work on new stuff 🤪
G39, MGT on the old stuff. Wouldn't it be in the HHT under Profile - Adjust?

You guys are making me feel old...I remember when REL, the DMR, then EPOCH 1 were state of the art...



   
ReplyQuote
(@chitownslick)
Joined: 1 second ago
Posts: 0
Topic starter  
I couldn't find anything in the tool that cotrolls the MG shutdown. I couldn'd find anything in the adjusting manual.
there must be something there that times out the generator when there is no demand.



   
ReplyQuote
(@chitownslick)
Joined: 1 second ago
Posts: 0
Topic starter  
FYI
I found what I needed.
MG shutdown is an internal timer set to 6 min. not adjustable.
The feature only works when the car is on normal, so if the inservice switch at the panel is off the MG never shuts down.



   
ReplyQuote