14/03/2012 8:34 am
911 guys.. Have a duplex unit with single "swing panel" controlling both units. Wired rope gripper control panels in and installed new relay boards from mce. They sent a new U9 chip which was installed and both units went nuts. Push car call 5 and car would go to 2 for example. Put old U9 chip back in and elev. 1 works fine. Elev 2 still has " stepping issues" 10 stops on both units. Elev. 2 will run from LL to 5 fine if I put a 6,7,8,9 floor call in unit will go to top floor slow down and hit top normal limit. We think that swapping the EEPROM chips around we need to readdress the floor designations?? Are we on the right track......thanks for any help
Topic starter
15/03/2012 7:08 am
Guys I feel so stupid, got the problem solved today.............broken travel cable wire for DZ.....used a spare and we are good.
15/03/2012 7:28 pm
hey there are no stupid questions!!!!...someone somewhere might have the same fault and you have might have saved them days of fault finding...and kept a customer happy and even in these days of tight budgets dare I say a contract!!!.
17/03/2012 11:38 am
Don't think you're special! Line forms to the left. We've ALL been there.
18/03/2012 6:29 am
The only "Stupid" question is the one not asked....
18/03/2012 7:38 am
we were always told 'id rather a stupid question than a disastrous mistake'.