If your going to use a motor especially an induction motor that's the same as line voltage, there's no benefit. Your control transformers are going to kick it down to 120 or less anyhow for all of the controls. And I've never seen a door operator run on higher than 220/240. Most new operators are fine with lower voltage.
100fpm 2500lb cap
HW is giving us a new 208/230/460 20HP motor .
AMPS - 29.2/28.2/14.1
With geared traction machine that says 7.3 HP
Your FLA amps to the motor would be higher. But if your motor HP is staying the same, the line current supplying the controller would not change. The only change in amperage you'd see is between controller to motor. The old setup the current supplying the controller was just as high before but was being supplied to the transformer primary, and on the secondary side (controller to motor) the amps were lower due to higher voltage. But power consumed is power consumed regardless of voltage.
I just don’t want to trip our main line breaker .. I think we should keep the existing transformer and the 480v to controller. This way amp is same as now
Keeping the transformer wouldn't hurt anything, but it is unnecessary. Unless you want to keep it for helping reduce harmonics. But if alpha is supplying a line reactor in the controller(they should be), that is sufficient.