LRVF mod

22 Posts
4 Users
0 Reactions
10.2 K Views
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776
Topic starter   [#36757]
Hi. I’m doing a traction mod. Old set up has 220 building power stepped up to 480v for Otis drive and motor. Is there any reason to keep the high voltage for new controller and motor ? Holister Whitney and Alpha seem to be fine with the 220v ?



   
Quote
(@elevatorman1966)
Eminent Member
Joined: 17 years ago
Posts: 33
 
the only reason someone would use high voltage machine / motor is to lower the Amps, what is the existing speed and capacity of the car ? if the HP is greater that 40HP or even 30hp its better to go with high voltage . smaller drive and better price on the controller , the down side is you need a step up transformer .



   
ReplyQuote
(@eelevator)
Honorable Member
Joined: 17 years ago
Posts: 579
 
Only reason to do that would be if the motor voltage is higher than line voltage. Alot of gearless pm motors are in the 300-400v range and if your line voltage is too low, the dc bus won't be able to charge to a high enough voltage to be able to run the motor.

If your going to use a motor especially an induction motor that's the same as line voltage, there's no benefit. Your control transformers are going to kick it down to 120 or less anyhow for all of the controls. And I've never seen a door operator run on higher than 220/240. Most new operators are fine with lower voltage.



   
ReplyQuote
(@eelevator)
Honorable Member
Joined: 17 years ago
Posts: 579

   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776
Topic starter  
The existing motor is 460v 10HP. With FLA= 14.3

100fpm 2500lb cap

HW is giving us a new 208/230/460 20HP motor .
AMPS - 29.2/28.2/14.1

With geared traction machine that says 7.3 HP

Last edited by Jluff; 02/02/24 05:35 PM.


   
ReplyQuote
(@eelevator)
Honorable Member
Joined: 17 years ago
Posts: 579

   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776

   
ReplyQuote
(@eelevator)
Honorable Member
Joined: 17 years ago
Posts: 579
 
This is true, if you halve your voltage and keep your hp the same your amperage will roughly double. I guess it depends on your goals. Is higher FLA bad? Wouldn't you just need to pull wires to the motor a little heavier?

Your FLA amps to the motor would be higher. But if your motor HP is staying the same, the line current supplying the controller would not change. The only change in amperage you'd see is between controller to motor. The old setup the current supplying the controller was just as high before but was being supplied to the transformer primary, and on the secondary side (controller to motor) the amps were lower due to higher voltage. But power consumed is power consumed regardless of voltage.



   
ReplyQuote
(@eelevator)
Honorable Member
Joined: 17 years ago
Posts: 579

   
ReplyQuote
(@montana)
Honorable Member
Joined: 17 years ago
Posts: 515

   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776
Topic starter  
Yes GT11.

I just don’t want to trip our main line breaker .. I think we should keep the existing transformer and the 480v to controller. This way amp is same as now

Last edited by Jluff; 02/02/24 07:14 PM.


   
ReplyQuote
(@eelevator)
Honorable Member
Joined: 17 years ago
Posts: 579
 
It doesn't make a difference to me what you end up doing, but I think your missing what I'm saying about power being equal. A transformer simply transfers power, it doesn't increase or reduce it. It changes the voltage/current relationship. The amperage is going to be the same through your disconnect regardless of whether you keep the transformer or ditch it. Because the voltage through the disconnect is not changing and the power required is not changing the current is not changing. The previous system only seen a reduction in current on the secondary side of the transformer, which is the controller side. This is why the data tag on a dual voltage motor has 2 amp ratings and 2 voltage ratings but only one HP rating. I'm speaking of Power in the electrical meaning of the word.

Keeping the transformer wouldn't hurt anything, but it is unnecessary. Unless you want to keep it for helping reduce harmonics. But if alpha is supplying a line reactor in the controller(they should be), that is sufficient.



   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776

   
ReplyQuote
(@eelevator)
Honorable Member
Joined: 17 years ago
Posts: 579
 
There is a couple potential perks to keeping the transformer, such as it serving as an iso transformer to help reduce voltage spikes as well as harmonics and maybe downsizing the drive to save a few bucks and saving a few bucks on motor wiring size



   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776

   
ReplyQuote