01/10/2016 3:33 am
Can I place the new door screen dry contact across terminals EP1 and EP2 or eliminate the EPD wiring and place the contact across the LRCU (Light Ray Curtain Unit ?)terminals, B4-B5; input IM3-4, RVD2.
I also note a resistor in parallel across the light ray contact. Is this typically existing or an option that needs to be added to a light ray setup. (Haven't checked out the I/O board yet)
Thanks!
02/10/2016 6:39 am
However you hook it up you just need to feed RVD2, just make sure you do not have a switch in front of the door detector contact as shown when using a LRCU that will disable your only reopening device. A parallel resistor across the contact is not necessary.
Topic starter
03/10/2016 9:41 pm
Thanks LA