Kone monospace 0026

7 Posts
1 Users
0 Reactions
8,988 Views
(@olugbemileke)
Joined: 1 second ago
Posts: 0
Topic starter   [#35004]
Hello all,

I have a monospace giving me 0026 when it stays idle for 15 to 20 minutes and resets once the elevator is restarted. I have done all advised on the fault sheet and yet same issue. Anything I am missing here?

Any suggestion will be appreciated.

Attachments
ERROR.jpeg (29.08 KB, 40 downloads)



   
Quote
(@OH boy)
Joined: 1 second ago
Posts: 0
 
Drive thermistor, is the fan working?



   
ReplyQuote
(@olugbemileke)
Joined: 1 second ago
Posts: 0
Topic starter  
Thanks for the response @OH boy

Drive is KDL 16L - it has no fan.



   
ReplyQuote
(@Fehlerteufel)
Joined: 1 second ago
Posts: 0
 
Hi,

I think this is the last error, what errors are before that.

If you have a problem with the PTC/NTC, look in the parameter for the motor temperature limit 6_67 and then the real time data from the motor 6_75-45, DCBL 6_75-41 and heat sink 6_75-40.



   
ReplyQuote
(@olugbemileke)
Joined: 1 second ago
Posts: 0
Topic starter  
Hi Fehlerteufel,

Thanks for your input.

I checked the motor temperature limit in 6_67 and it shows 120,
6_75 is 0

The only error it displays is 0026 when idle for less than 15mins.

However, after unplugging the XT1, it displays 0104.



   
ReplyQuote
(@Fehlerteufel)
Joined: 1 second ago
Posts: 0
 
hi,

So the thermo is recognized, that's good 😉.

In the 6_75 menu you can only activate the RealTimeData view individually, but not see it.

NOTE: RT display is moved behind Select key. From Floor
display; 1st Select key press enters Real Time Display, 2nd
Select key activates Car Speed Display. Displays selected
drive variable.

i have a few more ideas.

parameter lock (6_95) (0=open, 1=locked)
Set Standby mode (6_12) parameter to 0 (deactivates drive standby mode)
6_99 to 1 (save para) switch power off/wait/power on

Check if the error occurs again.

yes:
Check standby settings of cabin light, fan door drive. Deactivate individually for test purposes.

No:
Check all connectors (screw terminals), connections and shielding, PE !!!(electromagnetic interference) on KDL16 and motor.
Disconnect NTC and connect a resistor with 1.8kohm or higher.

Translated with www.DeepL.com/Translator (free version) 😉

Attachments
RTD KDL16_Screenshot 2023-03-31 133542_1.jpg (56.99 KB, 29 downloads)
RTD KDL16_Screenshot 2023-03-31 133056_1.jpg (270.4 KB, 21 downloads)
KDL16L_front.jpg (398.72 KB, 23 downloads)
KDL16L_side.jpg (397.53 KB, 21 downloads)



   
ReplyQuote
(@olugbemileke)
Joined: 1 second ago
Posts: 0
Topic starter  
Hi Fehlerteufel,

Update on the Kone monospace 0026

While Checking all connectors (screw terminals), connections and shielding, PE as you advised, including the brakes on the motor, i noticed some evidences of corrosion on the springs then I carried out comprehensive brake overhaul, (removal and cleaning of brake parts, confirmation of clearance and reassembling). After the overhauling, I returned the lift to normal and it performed the self test successfully after a while.

It has been doing well ever since.

Thanks so much for the assistance.



   
ReplyQuote