Topic starter
30/12/2019 8:03 pm
Neither the phase 1 or phase 2 key switch have any effect on the operation of the elevator. These key switches were functioning properly a month ago. Seems the system has dropped recall.
I'm uncertain how to check the parameter settings. Also do not know which parameter would need to be checked. I do not have any special tools for Kone.
Please let me know if there is something I can check through the menu system that is part of the controller.
30/12/2019 8:48 pm
Menu 1 sub menu 62 should equal 1
Topic starter
04/01/2020 4:44 am
Very helpful, that was what I needed. Thank you
Topic starter
04/01/2020 5:41 am
Is there a particular procedure to reset the controller after testing the oil timer?
04/01/2020 4:43 pm
Pull xm16 off for a few seconds